This is the capacitor bank that is currently installed.

It is an ABB C485G22.5-3FI capacitor bank connected to the service.
I didn't install it, but I think a capacitor may have failed in it.
I was trying to determine if it is sized correctly or needs to be upsized.
I am sure it's not the correct style unit for the service.

I had the following readings,

Phase A, 19.5a
Phase B, 12.5a
Phase C, 19.5a

A to B, 66.4?F
A to C, 100?F
B to C, 65.8?F
I think it's seriously shot.
At 22.5kVAr, the line current should be 27A.
Assuming the capacitors are connected in delta they each ought to be about 86uF.
If you measuse A to B at the terminals you will have that element plus the A to C and C to B both in series but the combination in parallel with A to C.
That would give a reading of about 130uF between any two terminals.
The capacitors are self healing. My understanding of this is that if the insulation between layers gets punctured, then the foil recedes from that thus reducing the effective area and consequently capacitance value.

Whatever, the unbalanced readings indicate that the unit clearly isn't healthy.
Replacement would seem to be the way to go. But maybe with a higher voltage unit.