Looking into the Federal Pacific K1XGF16-2 rated at 2kva. This is needed for a 1ph 208v primary to 1ph 240v secondary for a 50A appliance.
Looking at their voltage table (attached) that column (208v-236v @ 62.5A) shows a rating of 14.73Kva which makes sense. 236x62.5=14,750.
So where do these buck boosts get their label Kva rating from and why is it so much lower than what it can actually handle?
Edit: attached a screenshot to avoid downloading the chart pdf

K1XGF16-2 Federal Pacific 1 Phase 2 KVA | Power And Control Inc.
shop.powerandcontrol.com
Looking at their voltage table (attached) that column (208v-236v @ 62.5A) shows a rating of 14.73Kva which makes sense. 236x62.5=14,750.
So where do these buck boosts get their label Kva rating from and why is it so much lower than what it can actually handle?
Edit: attached a screenshot to avoid downloading the chart pdf