All listed receptacles have been tested for use at 100%.The Hubbell is 75°C termination rated isn't it? I also remember the Hubbell being rated for continuous use at 50A. I believe the others are 60°C and are not rated for continuous use at 50A.
All listed receptacles have been tested for use at 100%.
At the rate that these cheapo receptacles are burning up not long enough. Something needs to be done about the testing. No device should burn up under normal use within its rating.But for how long? And after how many thermal or mechanical cycles?
At the rate that these cheapo receptacles are burning up not long enough. Something needs to be done about the testing. No device should burn up under normal use within its rating.
They run the load taking temperature measurements at 5 minute intervals until there is no temperature rise for 3 consecutive measurement. I don't recall the permitted temperature rise, but the highest temperature recorded cannot exceed the temperature rise specified in the product standard.But for how long? And after how many thermal or mechanical cycles?
I’m sure they all past the tests out of the box.
Which is extremely likely in this case. Makes you wonder about the validity of the listing process.Note the the testing procedures are very specific. It is possible those do not match the real world usage of this product.
I would think running it at 100% and having a temperature rise of 30°C or less should reflect the type of usage. Give that the test continues so there is no additional temperature rise for 3 five minute intervals. The temperature is measured at the receptacle terminals and at the blade to socket connections.Which is extremely likely in this case. Makes you wonder about the validity of the listing process.
Perhaps the thermal environment of the test does not match the thermal environment of actual usage. Eg. if the test is done indoors in open air, that's different from being inside a box inside a wall filled with thermal insulation, possibly with solar heat gain on the exterior face of the wall, even when the indoor temperatures are the same.Not sure what else is going on.
A rep was at the supply house showing off new stuff told and me the problem was only with AL terminations, Leviton solved the problem by adding this wording to the EV receptacle:1450W
<p>50 Amp, 125/250 Volt, NEMA 14-50R, 3P, 4W, Flush Mtg EV Charging Outlet/Receptacle, Straight Blade, Industrial Grade, Weather-Resistant, Grounding, Side Wired, Steel Strap, Black</p>leviton.com
"Operating Temperature : -40°C to 60°C"
Straight Blade Devices, Receptacles, RTP, Industrial Grade, 3-Pole 4-Wire Grounding, 50A 125/250V, 14-50R, Black, Single Pack. | HBL9450A | Hubbell Wiring Device-Kellems
Designed for plug-in EV charging applications, Hubbell’s 14-50R receptacle is a premium and dependable solution to exceed the requirements of electric vehicl...www.hubbell.com
"Maximum continuous 75°C,"
What do you do when the male cord is part of the assembly?I have always used what I call a welder outlet, NEMA 6-50 receptacle for EV chargers (EVSE) that are not hard wired and not had any issue them.
I have yet to see a EV-charger (EVSE) that requires a neutral.
Gotta wonder how many of these failed devices go back to improper termination of the wires.
Most here know that if you tighten down the conductors then rotate the device to fit it in the box they will have loosened.
I make a point to turn the device 90 degrees to the right and left then re torque.
The continuous duty of these devices only magnify the poor connection.
A rep was at the supply house showing off new stuff told and me the problem was only with AL terminations, Leviton solved the problem by adding this wording to the EV receptacle:
"Wire Gauge : For use with #4, #6 or #8 AWG copper wire ONLY."
I just saw another one reported today. Guy says the receptacle was from Home Depot and in service for 3 years. Load was a 40A EVSE.