L.V. pool lights and land scape lights

Status
Not open for further replies.

M. D.

Senior Member
I have a customer that wants to put landscape lights on the same transformer as his pool lights. The Xfmer is an Intermatic px300 the pool light is 50 watts 12 volts. Would this be a violation of the nec??
 
The question is ; Can the xfmer supply both pool lights and landscape lights? I don't see where in 680 this would be a violation .
 
Did the landscape lights come with the pool lights?

Do the instructions for the pool light include the landscape lights?

Do the landscape lights come with their own transformer?

I think that you can find your answer in these three questions.

:)
 
No, its a listing issue not a code issue. Swimming pool transformers are listed for use with underwater fixtures not lighting systems operating at 30 volts or less which have power supplies listed for that purpose.
 
I hope this works ... not too good with computers.
http://www.intermatic.com/images/instruction_sheets/158t10532_px_transformers.pdf

This should be a link to the transformer that is employed . It can be used for pool lights and landscape lights , I'm not sure , do low voltage landscape lights always come with a transformer?? The pool lights did not but this transformer was recommended and was provided separately from the pool lights.
There is also nothing in the pool light instructions that say only the pool lights shall be connected to the transformer.
My instincts tell me it is not allowed ,but I can't find why or where

Perhaps 680.23(f)(3) 2005 is it??
 
Status
Not open for further replies.
Top