• We will be performing upgrades on the forums and server over the weekend. The forums may be unavailable multiple times for up to an hour each. Thank you for your patience and understanding as we work to make the forums even better.

L14-30 Outlet In-Use Cover?

Birken Vogt

Senior Member
Location
Grass Valley, Ca
Does anybody make an in use cover for an L14-30 outlet?

Pointing downward seems like the best option instead of like a bubble cover for a 15 amp outlet.

I am finding lots of generator inlet stuff, but none for an outlet.
 

winnie

Senior Member
Location
Springfield, MA, USA
Occupation
Electric motor research
You might need to hack something together, eg. buy an inlet box and then replace the inlet with a flanged outlet.


AC WORKS Super Durable Industrial Grade Electrical Outlet (Locking L14-30 30A 125/250V) https://a.co/d/8kat9LV

Many times the inlet and outlet components have the same dimensions
 

Todd0x1

Senior Member
Location
CA
Red Dot CKLSVU is 4-3/4 deep inside

edit: I don't think that will work though because the min bend radius on SOOW cord is 5x diameter which would be around 3in for 10/4, plus the 2.75" depth of the L14-30 plug. I think Winnie's solution is good.

Or instead of a locking plug could you use a 14-30R and right angle plug with a regular inuse cover?
 
Last edited:

kwired

Electron manager
Location
NE Nebraska
Occupation
EC
Most the 5-15 applications don't even allow cover to be closed with any sort of heavy duty plug and/or many heavier cords.

I understand the intent of the WPIU rule but practicality and intended use has never really existed with these.
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
Most the 5-15 applications don't even allow cover to be closed with any sort of heavy duty plug and/or many heavier cords.

I understand the intent of the WPIU rule but practicality and intended use has never really existed with these.
And millions of wasps thank the NEC for their new homes!
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Does anybody make an in use cover for an L14-30 outlet?

Pointing downward seems like the best option instead of like a bubble cover for a 15 amp outlet.

I am finding lots of generator inlet stuff, but none for an outlet.
You can usually just replace the inlet with an outlet
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
They are a completely watertight solution, better than a crappy plastic cover. Why wouldn't it qualify?
I didn't look closely at your link the 1st time. I thought it was just a flap cover and wouldn't protect while in use.
I see it requires a watertight locking plug.

So if you used both the receptacle and the plug in conjunction, it would be watertight.

My apologies.
 
Top