D DPW Member Location FT. SMITH, AR Jun 27, 2008 #1 Does all receptacles that are connected downstream of a GFCI receptacle have to be individually be labeled with 'GFCI PROTECTED' as desribed in 406.3 ('08 NEC)?
Does all receptacles that are connected downstream of a GFCI receptacle have to be individually be labeled with 'GFCI PROTECTED' as desribed in 406.3 ('08 NEC)?
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Jun 27, 2008 #2 Not if they have an equipment grounding conductor.