What is the code reference for labeling a GFCI protected receptacle?
R randelsink New member Location New Hill, NC USA Feb 14, 2014 #1 What is the code reference for labeling a GFCI protected receptacle?
Dennis Alwon Moderator Staff member Location Chapel Hill, NC Occupation Retired Electrical Contractor Feb 14, 2014 #2 There is no NEC reference other than 110.3(B). Now if these are receptacles with no ground as replacements then 406.4(D)(2) would apply
There is no NEC reference other than 110.3(B). Now if these are receptacles with no ground as replacements then 406.4(D)(2) would apply
Dennis Alwon Moderator Staff member Location Chapel Hill, NC Occupation Retired Electrical Contractor Feb 14, 2014 #3 I know that P&S gfci receptacles do not require the label but I have had an area around here that requires it. It is a "do it our way or you fail." BS
I know that P&S gfci receptacles do not require the label but I have had an area around here that requires it. It is a "do it our way or you fail." BS