Labeling of Panelboards
Isaiah
Baton Rouge
Electrical Inspector
The client has a number of 3ph, 4W 480/277V Panelboards he wants to use as power panels, that is, 480V 3ph 3W- no neutral. To me this is misleading but does it violate the NEC?
Can’t think of a reason why it would be an issue as long as the loads are straight 3phase.
The manufacturers label equipment based on their maximum possible voltage not on their supplied voltage.
If the source is 3 phase 4 wire a neutral conductor only needs to be present if there are Line -Neutral loads at that location.
I agree but it would be nice if the panelboard were field labeled 3Ø, 3W for anyone coming along in the future.
I would get an insulated neutral bar kit, and run the neutral, unless these panels are already installed
I have cursed aloud when needing to add a circuit, only to find the panel 10' away has no neutral:rolleyes: