wireday
- New England
- Master electrician
I have a lighting contactor with multiple breaker feeds.what should be put for warning on cover.I see they sell them online,but are pricey.Wanted to make some.thanks
There is no requirement to do so.
I often label the inside cover with all the circuit numbers.
I would individually number the hot and neutral conductors with the circuit numbers to make troubleshooting easier for the next guy.
I think you're probably kidding
He is not.
He works for an EC that does some very nice work.
He is not.
...multiple breaker feeds. what should be put for warning on cover...
Yes, I don't agree exactly with the others.
There is no definition of a contactor in Article 110, NFPA 70.
If you read Article 110, Industrial Control Panel(1), circuit breakers are listed in article.
If you go to Article 409.110 read it all, then (3) states what it states...
Or next week lol!I try to mark circuits also. Not because I wish to protect my fellow man but because I may end up working on the same circuits 5 years latter.