You mean zig-zagged back and forth through the holes? Probably not prohibited, but it may not qualify as "secured."celtic said:Would you consider MC/AC cables "laced" through the keyholes on metal studs (I'm talking vertically, not horizontially) a violation or not?
celtic said:Would you consider MC/AC cables "laced" through the keyholes on metal studs (I'm talking vertically, not horizontally) a violation or not?
[330.30]
Pierre C Belarge said:If any cable is laced through the metal framing, vertically, a portion of the installation will be in the "web" of the stud.
How are you maintaining the 1-1/4 inch spacing from the front of the stud?
Pierre C Belarge said:CJs or any other type of standoff will relieve that situation.
infinity said:If the cable is permitted to be run horizontally through the holes in the metal studs without being secured how is running vertically through the same holes any different?
Dennis Alwon said:It is one of those issue in the code where art. 330.30(C) only allows horizontal runs not vertical runs. Can you get called on it-- I believe you can. Do I think you should get called on it-- No I don't.
(A) General. Type MC cable shall be supported and secured
by staples, cable ties, straps, hangers, or similar fittings
or other approved means designed and installed so as
not to damage the cable.
(B) Securing. Unless otherwise provided, cables shall be secured
at intervals not exceeding 1.8 m (6 ft). Cables containing
four or fewer conductors sized no larger than 10 AWG
shall be secured within 300 mm (12 in.) of every box, cabinet,
fitting, or other cable termination.
(C) Supporting. Unless otherwise provided, cables shall
be supported at intervals not exceeding 1.8-m (6-ft)
Horizontal runs of Type MC cable installed in wooden
or metal framing members or similar supporting means
shall be considered supported and secured where such support
does not exceed 1.8-m (6-ft) intervals.
Dennis Alwon said:I thought that the vertical weaving was being done in lieu of fastening. I am not sure I am following this.
petersonra said:If you lace them through the studs vertically, they are for sure supported. You might need to secure them every 6 feet though, since there is some wiggle room on that. A few wire ties would handle it since wire ties are specifically mentioned as being an acceptable securing means.
celtic said:If they need additional securing every 6'....what's the point in lacing?
Perhaps, but in the field, they're just not flagging this type of installation in my experience. Once the cable is terminated to where ever it's headed, it's pretty darned secure in the middle of the stud when laced like that.petersonra said:But there could be some wiggle room for an inspector to say it is not secured.