You are happy that you are still getting it backwards? I am not in a trap, you are.Calculate the load. You fell into your own trap. Which make me happy.
Your load on one circuit may be the number of lamps powered by that circuit. But what about the next circuit over? And the next? How many circuits will there be? Well, that starts with a load calculation. Either on a ?watts per square foot basis? or on an actual lighting layout drawing (reflected ceiling plan) basis, you need to know the total load. Then you know how large a panel you need, and how large a feeder to that panel. Then you can make design choices regarding the number of circuits and the rating of each.My load is a number of lamps. Thanks to this thread I know this number. So I can go on to the sizing part as you say.
You say you know the number of lamps? I say you don?t. You haven?t told us if you plan to use a set of 20 amp circuits, or 30 amp circuits, or 50 amp circuits. You just latched on to the number 20 (or 19, or 17, or fewer, depending on which comment you are using for your number). Your design is not done yet.
I select a panel?s short circuit rating on the basis of the short circuit analysis. I require (in the specifications, not the drawings) that branch circuit breaker ratings must match or exceed the panel?s rating. As I said earlier, I don?t do a short circuit analysis of branch circuits.You select the breaker without a short circuit analysis?
If I am only adding branch circuits to an existing facility, perhaps never. If I am doing the design for an entire new building, then the short circuit, voltage drop, and fault coordination studies are nearly the last items on the task list.When do you do the short circuit analysis then??