Landing Cables

Alwayslearningelec

Senior Member
Location
NJ
Occupation
Estimator
If you have a 400A breaker can you run (4) 3/C #1 mc cables from it? Don't see why not.

How would that work landing multiple sets on the lugs? I know multiple sets are run all the time.

If there are 3 hots for each sets and there are 4 sets would each lug take 4 wires?
 
If you have a 400A breaker can you run (4) 3/C #1 mc cables from it? Don't see why not.
As Winnie stated you would need to check with the breaker manufacturer to see what options they offer for the particular 400 amp breaker. Otherwise a short run of 600 kcmil to a 5 port Polaris style connector might work.
 