Looking at a panel replacement, so have to deal with existing wire lengths. Siemens, in their wisdom, decided not to extend neutral bar the entire height of the columns of breakers.
Of course it's not that hard to extend wires using inline Wagos or the like. Speaking of which, is it ok to extend wires using soldered joints protected by heat shrink ? Wagos are clearly ok and easy, but solder joint seems more electrically "sound" - perhaps an issue for the excessively short neutral wire on a surge supressor such as https://www.eaton.com/us/en-us/skuPage.CHSPT2ULTRA.html given their exhortation to keep the leads as short as possible. (Seems likely it'd be good for the transmission-line characteristics of the wire to be uniform, to prevent reflections and such on the weird transients that might occur in a surge event, and certainly the soldered joint is more like a continuation of the wire than a Wago or a wire nut).
The feeder neutral is a different animal. What code section would you use to size this jumper?Hmmm. Wouldn't that also prohibit every feeder's neutral?
We have been considering such a jumper to be an extension of the neutral or the neutral bus.
Make it the same size as the neutral and there's nothing to calculate.The feeder neutral is a different animal. What code section would you use to size this jumper?
I agree that would ensure that it's safe but what code section would allow you to do that? You're creating a common neutral for multiple branch circuits.Make it the same size as the neutral and there's nothing to calculate.
In trying to answer you, I need to know why you believe that the same question does not apply to every sub-panel or feed-through-fed panel? What do you see as the functional difference?I agree that would ensure that it's safe but what code section would allow you to do that? You're creating a common neutral for multiple branch circuits.
Yes, but an upstream N-G bond is simply creating a NEC compliant parallel path. All other down stream, like in the panel after the bonding screw, are not compliant. It might seem like splitting hairs, but how far downstream would you allow?I think we've discussed this and not all agree. It's not a violation of 250.142(B) if done at the service equipment. And the enclosure may already be carrying parallel current if something like a meter socket is bonded to the grounded conductor upstream.
10 inches , max...Yes, but an upstream N-G bond is simply creating a NEC compliant parallel path. All other down stream, like in the panel after the bonding screw, are not compliant. It might seem like splitting hairs, but how far downstream would you allow?
Be that as it may, I see it done quite often. If one is adding an ATS ahead of a panel where the grounds and neutrals have been mixed, separating them is a discomfort in the nether regions.Electrically it would only be ok with a jumper between the neutral bar and the ground bar. In short with the jumper, it would be like extending the neutral bar.
But in the real world I doubt any inspector would go along with this and yes it probably would violate the panels instructions.
On top of that there is no good reason to do it and it would be confusing.
True, but still required. I've done it plenty of times, and made sure to include it in the contract.Be that as it may, I see it done quite often. If one is adding an ATS ahead of a panel where the grounds and neutrals have been mixed, separating them is a PITA.
Does Siemens make a connector to add a neutral below those short ones?
True but it is not known if the add on neutral bar is connected (bonded) to the panel or has insulators. It must have insulators as the panel could be used as a sub panel.Bing bing bing, we have a winner. Not in the list of accessories on the label, but in the schematic ...
Actually, looking at the way the factory-installed neutral bar is installed, it's definitely insulated from the panel. Moot if the panel is first means of disconnect and ground and neutral are bonded.True but it is not known if the add on neutral bar is connected (bonded) to the panel or has insulators. It must have insulators as the panel could be used as a sub panel.
To be clear, this one absolutely DOES come with enough capacity. It's just that there's a paucity of both ground and neutral terminals at the end farther from the main breaker. Less than $100 solves that problem, but that's annoying.It just bugs me that every panel doesn't come with enough ground bar and neutral bar capacity on *each* side to accommodate a maxed out panel.
I draw the line around the service equipment enclosure. It's not 'downstream' or 'upstream' if you're in the same box.Yes, but an upstream N-G bond is simply creating a NEC compliant parallel path. All other down stream, like in the panel after the bonding screw, are not compliant. It might seem like splitting hairs, but how far downstream would you allow?
Nothing. Just like the cleaner look. It is worth almost $100, hmm ...What's wrong with wire and wire-nuts?
SE's coming in from bottom.Or mount it main down if it works better.
Service conductors? And most of your circuits? Then definitely install it main breaker down!Nothing. Just like the cleaner look. It is worth almost $100, hmm ...
SE's coming in from bottom.