For a job I am working on, we need to install a large chiller. The chiller's spec sheet lists a MCA of 729.2 amps and a MOCP of 1000 amps. We designed our conductors for 760 amps, and specified a 1000 amp circuit breaker from the MDP. We got pushback from the electrical contractor, saying that our feeders were undersized (he did not give a code reference, just told us we were wrong and to redo it). We were referencing 110.3B, as the provided equipment listing we were required to follow was satisfied in both the MCA and MOCP. However, when I went back through the NEC to double check our work, I came across 240.4C. Per 240.4C, since the overcurrent device is over 800 amps, we need to size the conductors at or above the rating of the overcurrent device.
I understand that since MCA is the minimum amount of ampacity the conductors need to be able to handle, conductors sized for 1000 amps would also satisfy the manufacturer's listed requirements; upsizing the conductors would carry a cost increase and new set of drawings that I'd like to avoid if possible.
My question is: are we okay just following the manufacturer's listing or does 240.4C override that in our case?
Thanks for the help!
For a job I am working on, we need to install a large chiller. The chiller's spec sheet lists a MCA of 729.2 amps and a MOCP of 1000 amps. We designed our conductors for 760 amps, and specified a 1000 amp circuit breaker from the MDP. We got pushback from the electrical contractor, saying that our feeders were undersized (he did not give a code reference, just told us we were wrong and to redo it). We were referencing 110.3B, as the provided equipment listing we were required to follow was satisfied in both the MCA and MOCP. However, when I went back through the NEC to double check our work, I came across 240.4C. Per 240.4C, since the overcurrent device is over 800 amps, we need to size the conductors at or above the rating of the overcurrent device.
I understand that since MCA is the minimum amount of ampacity the conductors need to be able to handle, conductors sized for 1000 amps would also satisfy the manufacturer's listed requirements; upsizing the conductors would carry a cost increase and new set of drawings that I'd like to avoid if possible.
My question is: are we okay just following the manufacturer's listing or does 240.4C override that in our case?
Thanks for the help!