I pick grounded wye...
I pick grounded wye...
I grew up in the paper industry with multiple 1500 & 2500 kVA substations with 480V secondaries and they were all ungrounded delta. There was no need for 277 Volts. And in my 15 years at that plant site, there were no apparent instability problems on the secondaries of the transformers.
But logic tells me today that it's an inherently more stable and safer system if the secondary is a grounded wye, if the transformer has that ground reference.
There's no need to bring the neutral conductor past the switchgear, so the wiring to the 480V motors is the same as if it were a delta system.
And the conduits/grounds are referenced back to the transformer, so faults are provided with a positive path back to the transformer.. unlike the ungrounded delta.
Fault current will be high given the 2400 HP of motor loads. I think this installation needs a minimum 3000/3500 kVA transformer, and perhaps higher depending on the motor starting means. That translates to 85 kA rated equipment.
IMO, high-resistance-grounded systems are reserved for those installations where power continuity is critical, i.e. data centers, hospitals, etc. They require a significant detection system, as well as personnel experienced in troubleshooting that type of system.
I think I'd stay with the conventional grounded wye system, from a stability and safety standpoint - unless someone gave me a delta secondary transformer.
JM