OK, I think of a "supply side connection" as effectively being a service with only the PV on it. So once you add some loads, it's no longer a supply side connection, it's just a second service. I think the terminology would be cleaner if the whole "supply side connection" stuff went away, and it was just treated as a service.
Is there anything that (2020) 705.11 allows that you can't do under (2020) 705.12 via a feeder interconnection just after the (distribution less) service disconnect?
Cheers, Wayne
Is there anything that (2020) 705.11 allows that you can't do under (2020) 705.12 via a feeder interconnection just after the (distribution less) service disconnect?
Cheers, Wayne