One of the large chillers I am responsible for is VFD driven and powered by an ungrounded 480 delta, This is in the 500 HP range. We have seen some unusual dark spots on the motor windings, and unusual wear on the motor shaft thrust ring and bearing surface. The motor megs fine, and was additionally tested by a very reputable motor shop.
I'd like to hear from those knowledgeable about VFDs on an ungrounded system.
I know that more than one manufacturer advises to not use their VFD on an ungrounded system, since ther is no real ground reference in the system, and fault current would be phase to phase, not necessarilly phase to ground unless there were ground faults on more than one phase. We have found no signs of unintentional grounding, but the anaomalies I wrote of remain.
Thanks to all for your comments.
I'd like to hear from those knowledgeable about VFDs on an ungrounded system.
I know that more than one manufacturer advises to not use their VFD on an ungrounded system, since ther is no real ground reference in the system, and fault current would be phase to phase, not necessarilly phase to ground unless there were ground faults on more than one phase. We have found no signs of unintentional grounding, but the anaomalies I wrote of remain.