Is it required to include this load on a service calculation in a dwelling if will not contain a dryer? 220.54
I have someone telling me that I have to include it no matter what.
The way I read it it only applies if you have an electric clothes dryer. I am not sure a laundry is required at all in a dwelling.
I suspect if you have a laundry it will require either an electric connection or gas connection for the dryer. But probably not both.
That's not quite the same thing as saying you meet one of the two exceptions I mention above. Take a look at the wording of those two exceptions, and let us know what you think.The house in question does not have a laundry room
I don’t think 210.52(F) would even apply to my situation. There is no laundry room in the home. You would only be able to put a washer and dryer in the garage.This is trickier than I expected. 210.52(F) requires a receptacle outlet for laundry, but it includes two exceptions. If you meet one of the exceptions, then 210.11(C)(2) will not require you to include a circuit for the laundry. That brings us to 220.54. It includes the words, “for each dryer served.” Thus, if you meet one of the exceptions, then there will be no dryer served, and you don’t have to include 5000 VA in the load calculation.
But I would be careful with using this reasoning. The present owner might not allow laundry in the building, but the next owner might. My engineer’s instinct would be to toss the 5000 VA into the calculation, and see the extent to which it might alter the final result. If it makes no difference to the service equipment rating, then I would leave it in. If it changes the service from a 1000 amp to an 1200 amp, then I would have a conversation with the owner.
I don’t think 210.52(F) would even apply to my situation. There is no laundry room in the home. You would only be able to put a washer and dryer in the garage.
It seems to me you are conflating the 210.52(F) 120V receptacle for a laundry (that 210.11(C)(2) says has to be on a 20 amp circuit, and 220.52(B) says has to be calculated at 1500VA) with a 240V 30A receptacle for an electric dryer. I see nothing that requires the installation of an electric dryer or a circuit for an electric dryer. 220.54 simply says that if an electric clothes dryer is served, it has to be calculated at a minimum of 5000 VA. So no electric dryer, no 5000 VA (but still 1500 VA for the laundry circuit).This is trickier than I expected. 210.52(F) requires a receptacle outlet for laundry, but it includes two exceptions. If you meet one of the exceptions, then 210.11(C)(2) will not require you to include a circuit for the laundry. That brings us to 220.54. It includes the words, “for each dryer served.” Thus, if you meet one of the exceptions, then there will be no dryer served.
This is trickier than I expected. 210.52(F) requires a receptacle outlet for laundry, but it includes two exceptions. If you meet one of the exceptions, then 210.11(C)(2) will not require you to include a circuit for the laundry. That brings us to 220.54. It includes the words, “for each dryer served.” Thus, if you meet one of the exceptions, then there will be no dryer served, and you don’t have to include 5000 VA in the load calculation.
But I would be careful with using this reasoning. The present owner might not allow laundry in the building, but the next owner might. My engineer’s instinct would be to toss the 5000 VA into the calculation, and see the extent to which it might alter the final result. If it makes no difference to the service equipment rating, then I would leave it in. If it changes the service from a 1000 amp to an 1200 amp, then I would have a conversation with the owner.
(F) Laundry Areas. In dwelling units, at least one receptacle
outlet shall be installed in areas designated for the installation
of laundry equipment.
Not my intent. I was using a path of reasoning that led me to conclude that it was OK for there not to be a dryer, on the basis that there was no need to have a laundry circuit in the first place.It seems to me you are conflating the 210.52(F) 120V receptacle for a laundry . . . with a 240V 30A receptacle for an electric dryer.
I agree with this.I see nothing that requires the installation of an electric dryer or a circuit for an electric dryer. 220.54 simply says that if an electric clothes dryer is served, it has to be calculated at a minimum of 5000 VA. So no electric dryer, no 5000 VA.
Not necessarily, as I have already said.. . . (but still 1500 VA for the laundry circuit).
It seems to me you are conflating the 210.52(F) 120V receptacle for a laundry (that 210.11(C)(2) says has to be on a 20 amp circuit, and 220.52(B) says has to be calculated at 1500VA) with a 240V 30A receptacle for an electric dryer. I see nothing that requires the installation of an electric dryer or a circuit for an electric dryer. 220.54 simply says that if an electric clothes dryer is served, it has to be calculated at a minimum of 5000 VA. So no electric dryer, no 5000 VA (but still 1500 VA for the laundry circuit).
Cheers, Wayne
+1.I would argue this. 210.52(F) requires an outlet in areas designated for the installation of laundry equipment. if there is no laundry, no outlet is required. If there is no laundry, there is no dryer, so no dryer outlet required.
Right, I should have said the 1500VA is required if there is a laundry area.Not necessarily, as I have already said.
I believe that changed with the 2014 NEC:There are only a few cases where you the requirement for a laundry is permitted to be omitted.
Which edition of NEC applies. As just mentioned a couple posts back - 2014 seems to require you to figure in 1500 VA for laundry unless you meet exceptions, even if you don't have a "laundry area".So I am to understand that I don’t even need the 1500va in the calculation for a laundry outlet since neither structure has a “laundry room”?