I’m on 2017 code hereSo I am to understand that I don’t even need the 1500va in the calculation for a laundry outlet since neither structure has a “laundry room”?
I believe that changed with the 2014 NEC:
The 2011 wording for 210.52(F): "In dwelling units, at least one receptacle outlet shall be installed for the laundry." Meaning, unless you meet one of the exceptions, you need a laundry receptacle outlet, even if you don't have a laundry.
The 2017 wording for 210.52(F) (no gray markings, so presumably the same in 2014): "In dwelling units, at least one receptacle outlet shall be installed in areas designated for the installation of laundry equipment". Meaning, if you don't want a laundry receptacle, don't designate any areas for the installation of laundry equipment.
Cheers, Wayne
Without the dryersThat sounds to me like a 2-family dwelling. You can meet exception 2 to 210.52(F) by having the owner declare that laundry is not to be allowed on site. That brings you to the reasoning I first posted, from which you can conclude that you don't need to include, in your calculation, a dryer when there is no dryer to be served.
By the way, are the 122 and 77 amp values with, or without, the dryer?
Is it required to include this load on a service calculation in a dwelling if will not contain a dryer? 220.54
I have someone telling me that I have to include it no matter what.
The 2011-2017 NECs all have the same version of 210.11(C)(2): "In addition to the number of branch circuits required by other parts of this section, at least one additional 20-ampere branch circuit shall be provided to supply the laundry receptacle outlet(s) required by 210.52(F)." However, as discussed above, the 2014 and 2017 versions of 210.52(F) do not require any laundry receptacle outlets if you don't "designate" any areas "for the installation of laundry equipment."Greetings,
1) it is my opinion that since you are talking about a one- family dwelling, the laundry branch circuit demanded by 210.11 (C)(2) is required and the 1500VA is required by 220.52 (B).
So in that case, how do you interpret 210.11(C)(2)'s call for at least one branch circuit to serve zero receptacles? I would say that is nonsensical and that zero branch circuits are required, meaning no 1500VA allowance is required.
Cheers, Wayne
The issue I see isn't the exceptions, it is the 2014 change in the language of 210.52(F) to require laundry receptacles only in "areas designated for the installation of laundry equipment." If I don't want any laundry equipment, and don't want to install any laundry receptacles, I'm free under the new language not to designate any area for the installation of laundry equipment.the exceptions to 210.52 (F) do not apply to my scenario
I can agree that in order to "undesignate" the area, the washer and dryer should be removed, and the water supplies and drain should be capped. I would say that having functioning laundry hookups would count as designating the area.So a house that had a washer and dryer in an area that was indeed designated now is to be "undesignated" in order to meet a new load calculation.
If I were more motivated, and the TerraView software wasn't so unfamiliar, I would look up the track record of that 2014 change in language.
Cheers, Wayne
I think at this point the only opinion that will matter is the local AHJ. You may be able to convince the AHJ by removing the existing branch circuit for the dryer completely and build your argument around the position of "If no dryer circuit exists then no load need be considered". However, he/she is the one you need to convince of this position.The owner of this property is more than willing to ditch the washer and dryer in the garage if it will accommodate not installing a upgraded service. The house is just a rental and he can’t justify the cost of upgrading when all he needs to do is simply not offer a laundry. It would envolve digging ditches, cutting concrete and upgrading the transformer at the utility. I can only imagine what that would cost. The no laundry option is the best option for him.
The exceptions in 210.52 (F) are no help to you in my opinion.
Good Luck!
LOL.....Even the best expressed plans don't always go as planned.The code is the code in my option. I certainly hope it doesn’t come down to luck.
Maybe hope is not lost yet.The code is the code in my option. I certainly hope it doesn’t come down to luck.
Tap out your loads for each building or attach a PDF and possibly someone can help you get your totals down even with the 5000 included for the dryer.