Looking to get some clarifications on 2020 code requirements. Doing a laundry room and this is what I’ve come up with...
30 amp 240v dryer receptacle will need Gfci protection- fed from main
20 amp 120v laundry receptacle will need arc fault/ Gfci protection- fed from main
20 amp 120v laundry convenience outlets need arc fault/ Gfci protection, and only serve the receptacles inside laundry room. -fed from 50a sub circuit 2
20 amp 120v-outside receptacles and lights
receptacles will be WRgfci. Outside lights are fed of line side of outside Gfci- fed from 50a sub circuit 4
30 amp 240v heater- heater will be hard wired. Heater is 5000watts/240v=20.83X 125%= 26.03 fed from 50a sub circuits 1/3 not sure if I’m missing anything for the heater.
that’s what I came up with after looking through my book. Again any and all help is appreciated!