No, the NEC does not require that.Do all LAYIN LIGHTS NEED TO HAVE WIRE SUPPORT ? 2020 NEC ?????????????????????????????????????????????????????????????????????????
But other codes may require support wires that are attached to the luminaires.410.30(B) Suspended Ceilings.
Framing members of suspended ceiling systems used to support luminaires shall be securely fastened to each other and shall be securely attached to the building structure at appropriate intervals. Luminaires shall be securely fastened to the ceiling framing member by mechanical means such as bolts, screws, or rivets. Listed clips identified for use with the type of ceiling framing member(s) and luminaire(s) shall also be permitted.
Thank you .No, the NEC does not require that.
But other codes may require support wires that are attached to the luminaires.