layin light fixture terminations

Status
Not open for further replies.

ktollar

Member
Can you daisy chain mc cable for connection of lay in flourecence lights in an office building ceiling? Do these fixtures have to have the disconnect in them? Is the maximum lenghth 6' for the mc cable to a j-box?

NEC 410 and 330
 

jwjrw

Senior Member
Yes you can daisy chain them with mc
Yes a disconnect is required in commercial buildings.
It's 6 ft maximum unsupported on your whips.
 

cadpoint

Senior Member
Location
Durham, NC
Yes you can daisy chain the light wipes if you support them over six foot in length.

Yes, the manufacture supplies in most cases (new installs) the little disconnects, if not you'll need to install this device if you move the equipment.
 
Last edited: