Modern addressable ones can handle a lot more dirt than the older ones. They adjust for the dirt build up, and when they get too dirty, give a trouble alarm, not a fire alarm.Smoke detectors get dirty and cause false trips.
That rule only applies to the AC supply for the FA control panel. Unless you have local codes then you can "free air" the FA low voltage cable without conduit.Originally posted by eeee:
4.4.1.4.2 Mechanical Protection.
4.4.1.4.2.1 The dedicated branch circuit(s) and connections shall be mechanically protected.
don_resqcapt19 said:eeee,
I'm sorry but in my opinion, he is wrong. It is very possible for the people to be dead from the smoke before the first sprinkler head releases any water. Even if that is not true, there are very few fires where a sprinkler head will open before a smoke detector alarms. Again, in general, fire alarms protect people and sprinklers protect property.Our fire chief indicates he perfers sprinkler system for protecting people better since they start fighting the fire before the fire department gets there.
Don