The way I read 314.28(A)(3) is that you are permitted to have a conductor fill in the LB less than what Chapter 9 Table 1 allows provided that the conduit body is listed for, and is permanently marked with, the maximum number and maximum size of conductors permitted.
This section does not allow the LB to just be sized per Chapter 9 Table 1 it allows the manufacturer to specify the largest size and number of wires permitted in the LB provided that the fill does not exceed Chapter 9 Table 1 fill limits.
Chris
I think we are in agreement. If the conduit body is marked with a maximum conduit fill and if you don't exceed the fill requirements of Table 1 Chapter 9 then it is compliant. Correct ?
I guess I am still a bit confused. If I have a 2" LB in a 2" conduit run and the LB is marked "Max 3-2/0 XHHW", but I am installing 5-1/0 THHN & a #4, since that fill is allowable in the 2" conduit, does this male them allowable in the LB ?