S solarken NABCEP PVIP Location Hudson, OH, USA Occupation Solar Design and Installation Professional Yesterday at 12:13 PM #1 Any manufacturer make LB's with EGC binding screw inside for terminating wire-type EGC when transitioning from PVC conduit to EMT?
Any manufacturer make LB's with EGC binding screw inside for terminating wire-type EGC when transitioning from PVC conduit to EMT?
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Yesterday at 12:24 PM #2 I've never seen one. Might need to drill your own hole. The EGC doesn't run through the EMT?
R Rock86 Senior Member Location new york Occupation Electrical Engineer / Electrician Yesterday at 12:40 PM #3 As long as you are not installing EMT in between sections of PVC without ever bonding the EMT, then if your EMT is installed properly, it should be bonded for the whole length including the LBs when the EGC is bond to an enclosure.