Any manufacturer make LB's with EGC binding screw inside for terminating wire-type EGC when transitioning from PVC conduit to EMT?
If the EGC enters from PVC conduit, into metallic LB, termination there could permit the EMT exiting the LB to be the EGCI've never seen one. Might need to drill your own hole. The EGC doesn't run through the EMT?
I don't think you read the part about transitioning from PVC to EMTAs long as you are not installing EMT in between sections of PVC without ever bonding the EMT, then if your EMT is installed properly, it should be bonded for the whole length including the LBs when the EGC is bond to an enclosure.
I did read that. What I was saying is that if you go PVC - EMT - PVC, then you would need to bond the EMT. If you have an EGC in conduit that goes PVC - EMT, then the EMT should be bonded at the next metal enclosure.I don't think you read the part about transitioning from PVC to EMT
I think I will just use a Metal jbox and transition the EGC there. Thanks.@solarken
Never seen one . Probably have to drill and tap 10/32 tap #21 drill.
Or use a junction box?
With respect to the OP that sounds like a shoty thing to do. is it really that much of a cost savings to not run the EGC the whole length? I wont disagree that it would be code legal to add the box and make the bond, but I wouldn't be a fan of it.The OP wants to use the EMT as the sole EGC in that section of the run, so the bonding is necessary to change over from the wire type EGC to the EMT type EGC.
Cheers, Wayne
Not sure I understand why you think it is shoty. EMT or rigid conduit is a permitted EGC. There are situations with long runs where including a wire-type EGC inside EMT would require upsizing to the next size vs just using the EMT as the EGC. There are also situations where it might be advantageous to not have to terminate a bunch of wire-type EGC's, such as in a metal wiring trough where you can avoid having to install a ground bar. Also, if circuit conductors are increased in size for voltage drop reasons, EMT as the EGC does not have to be proportionally increased in size like wire-type.With respect to the OP that sounds like a shoty thing to do. is it really that much of a cost savings to not run the EGC the whole length? I wont disagree that it would be code legal to add the box and make the bond, but I wouldn't be a fan of it.
I think it is shoty to go from PVC to EMT and no continue the EGC. I understand what you said, but if I started the run with an EGC, i would continue it regardless. If I were to come make a repair after you were long gone and I saw an EGC on one but not the other, it could make for a waste of time tracing out where the EGC went.Not sure I understand why you think it is shoty. EMT or rigid conduit is a permitted EGC. There are situations with long runs where including a wire-type EGC inside EMT would require upsizing to the next size vs just using the EMT as the EGC. There are also situations where it might be advantageous to not have to terminate a bunch of wire-type EGC's, such as in a metal wiring trough where you can avoid having to install a ground bar. Also, if circuit conductors are increased in size for voltage drop reasons, EMT as the EGC does not have to be proportionally increased in size like wire-type.
I wasn't an English major. hahahaTo each their own, personally I think the word "shoty" is shoddy
Was the metal thick enough to have a full 2 thread engagement?I've drilled and tapped conduit bodies before. Could have been because the PVC one I needed was a 100-mile round trip.
A little oxide inhibitor on the ground screw threads and you're good to go.
Absolutely.Was the metal thick enough to have a full 2 thread engagement?