What is the real hazard in overcorrecting PF with excessive capacitance, resulting in a leading PF? I probably should be able to answer this myself, but school was so, soo, sooo long ago.
What is the real hazard in overcorrecting PF with excessive capacitance, resulting in a leading PF? I probably should be able to answer this myself, but school was so, soo, sooo long ago.
Probably even longer ago for me, young fellow.......What is the real hazard in overcorrecting PF with excessive capacitance, resulting in a leading PF? I probably should be able to answer this myself, but school was so, soo, sooo long ago.
Possible rather than probable.depends
if local at the motor and left online when motor is turned off severe resonant at a f > 60 hz
likely motor and swgr damage
Possible rather than probable.
Off is off.
Unless you go too extreme, utility probably doesn't care - less correction they need to apply on their own. Yes they still put their own correction capacitors in their distribution where they feel is needed. Larger industrial type customers are mostly the ones paying penalties for poor power factor, residential and other smaller services typically are not forced to correct poor power factor - so there still is poor PF within the system and they do place capacitors in the system to lessen the effects.I don't think there is any harm in doing so. Each load is getting the correct amount of power that it needs, and the excessive reactive power is being pushed back onto the grid. The utility doesn't like it, but I don't think there's any harm in it.
Correct me if I'm wrong though, anyone
A little tale for you that I have posted here before.likely, almost certain
To be NEC compliant though you must have discharge resistors installed on the capacitor.A little tale for you that I have posted here before.
A good many years ago we had the bright idea that we could run a submersible pump and induction motor in reverse. The pump running as a turbine and the induction motor as an induction generator. The idea was cheap power where there was no utility grid.
I set it it up in our test bay with a variable speed DC drive as the prime mover in place of the pump/turbine.
As I'm sure you know, just spinning an induction motor won't make it a generator. It needs excitation. Enough residual and a PFC bank worked a treat. I got it up to 30kW which was the rating of the machine. All good. And no severe resonances.
Perhaps a more relevant point here is that if you leave PFC connected to the motor when the supply is disconnected and the motor load can drive it you can get regeneration, desirable or otherwise. That's why we, and other responsible manufacturers, always include a contactor for the PFC bank.
PFC units normally come with pre-fitted with discharge resistors.To be NEC compliant though you must have discharge resistors installed on the capacitor.