100310-1504 EST
If we can assume that that the leakage is from hot or neutral to the enclosure of the refrigerator (or whatever), and there is a 3 conductor cord to the appliance with hot, neutral, and EGC as the wires, and that EGC is connected to the enclosure, then make an adapter as follows:
Three prong socket and plug. Connect hot and neutral straight thru with individual wires. Between the two EGC terminals put a 1 ohm 1 W resistor. If there is much over 1 A on the EGC wire the resistor will burn up. Put a digital voltmeter across the 1 ohm resistor. MV translate to MA. This technique saves burning out expensive fuses in the current mode of DVMs in the case of a large unexpected current.
For this test to work the enclosure must not have any conductive path from the enclosure that would bypass the current measuring resistor.
.