U2cy2
- Charlottesville Va
I have a clinic that has all LED lighting and we use Square D panels. One of the lighting circuits it pretty well loaded, 15A on a 20A breaker. This breaker get pretty warm to touch and I have taken infrared photos of the breaker. We have changed the breaker out and even moved its location but the condition follows. The breaker has never tripped out. The attached photo is showing a lower amp/heat reading than what I have seen but it is telling a story, just the same. There are other all LED luminaire circuits in this panel but they are not loaded as much as this circuit and are not getting hot.
I contacted Schneider Electrical for technical assistance on why the breaker is getting this hot within an air conditioned space (mid 70˚s f) and this is their reply:
“Hi Steven,
For the load in question, you may want to try the QO120HID type breaker as it has a different contact construction designed for high pressure sodium and metal halide type lighting circuits. Has the breaker tripped or is the concern the heating effect in the panel itself? The temperature rise limit of breakers under UL is 50C above ambient. So if your breakers are in a 25C environment, the limit would be 75C - you are at 46C.”
My question to you is with the circuit being all LED luminaires is the heat I am seeing coming from harmonics, due to all electronics load? Or would this be seen on the neutral only?
I have other clinics that have all LED luminaire circuits that are showing signs of heat compared to the other circuits within the panel (Square D as well) but not as hot as this circuit. To me this is a concern because it is above the “norm” and it is happening in a medical clinic, so it draws extra attention from me.
Have checked the screw (wire/breaker) connection and it meets the torque specs for this breaker.
What are your thoughts? I am more interested on why it is generating heat and how to prevent it from happening in the future than a fire hazard (at this point at least).
I, also, have asked the electrical engineers that designed the circuits what could be causing the heat but got the standard engineers answer when they don’t have a clue.
“Hi Steven,