LED Lighting ...

Status
Not open for further replies.

1793

Senior Member
Location
Louisville, Kentucky
Occupation
Inspector
I have a situation that I would like to have a little help with.

I have 4 LED mini recess luminaires, 3w each. I have 2, two, drivers one with 3 terminals and 1 single. The drivers require Electronic Low Voltage dimmer.

The dimmer I need to use is a Leviton VIZIA+ VPE04-1L 400w The instruction call for a minimum of 40W.

I'm looking for a way to add the additional load to this setup.

I would greatly appreciate any input.

As always, thanks in advanced.
 

J.P.

Senior Member
Location
United States
Can't use a smaller dimmer?

I looked that up and didn't see a minimum listed.
I usually use lutron devices and have never noticed a minimum on those either.

  • Product Features
  • Style Name: Vizia +
  • Switch Type: Single-Pole, 3-Way or More Applications
  • Type: Digital
  • Load Type: Electronic Low Voltage
  • Load Rating: 400W
  • Voltage: 120 Volt AC 60Hz
  • Light: LED Locator and Brightness Display
  • LED Color: Green
  • Protection: Radio/TV Filter
  • Wallplate: Order Separately
  • Warranty: 5-Year Limited
  • Standards and Certifications:UL/CSA
  • Color: White Ivory Light Almond
  • Color Change Kit: VPKIT-MD
  • Available Color Kits: Ivry-I Wht-W Almnd-A Gry-G Blk-E Brwn-B LA-T
 
Last edited:

gar

Senior Member
Location
Ann Arbor, Michigan
Occupation
EE
150513-1946 EDT

1793:

At http://www.leviton.com/OA_HTML/ProductDetail.jsp?partnumber=VPE04-1LZ&section=47398 pick and open Product Specification and Data Sheet.

Find Figure 2. This shows a neutral connection. I suspect that when wired this way with the neutral connection that there would be no minimum load requirement.

Operate one of these dimmers with no-load using the neutral connection and use a scope or voltmeter to observe operation.

Add a small load like 15,000 ohms at 1 W rating, and see if you get smooth control and that the voltage measured or waveform is about the same as with no load. Then try with a small incandescent load. If everything seems smooth, then try with your LED load.

.
 
Status
Not open for further replies.
Top