I have a customer that experienced flickering lights daily for 11 MONTHS and spent 4 figures with various electricians with negligible results. We then tightened every wire-nut junction and device termination in the house, re-torqued all panel connections and added a good SPD. Monitored and recorded the service entry and added second ground rod. Improved, but did not totally clear the problem. As a last resort, we zeroed in on the AC Unit, adding a new Service Disconnect and ran AWG 8 stranded copper, THHN, 2 conductors in rain-tight conduit almost 90 feet from the unit to the panel, and kept the existing10/2 Romex in parallel.
Full-load voltage drop came in at under 1% and the problem has never shown up again (so far - 3 months).
I am giving him a 5-year workmanship warranty with confidence.
Your thoughts, anyone?