LED Load

Status
Not open for further replies.

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
So how would you go about figuring the load for this fixture? Not much info on the driver?

http://www.innovativelight.com/wp-content/uploads/2013/11/Smooth_LED_Light_C_Series_2x2.pdf

Driver and LEDs seem to replace existing tubes and ballasts, so input would be whatever AC voltage was originally used, up to a max of 277V.
The energy given could be into driver or delivered to the LED units.
I would figure at least 90% efficiency and power factor of .9 unless I could get better info from the specs.
 