malachi constant
Senior Member
- Location
- Minneapolis
I am the specifying engineer on a project where we are replacing lay-in fluorescent troffers one-for-one with LED troffers. Troffers are Columbia LCAT24 style (fairly standard architectural lay-ins).
The electrical inspector is prohibiting the installation because the fixtures are close enough to the structure above that "an electrician cannot get access to the junction box of the fixture without needing to bring the entire fixture down". The existing fluorescent fixtures (that were wired through knockouts on the fixture ends) were legal per the electrical inspector, because you could get access to the wiring by opening the door. I have not been to the site yet to view the new fixture.
We have the option to retrofit the fluorescent housing. The existing fixtures have not yet been removed, and the client has enough lighting replacement projects in the works that the LEDs would have a home by next summer. So this isn't that painful. But it's weird, as one of the original selling points for LED troffers was you can slip them into tighter ceilings. It's one more thing I would have to wonder about when looking at replacement of an existing recessed system, and the less things I have to wonder about the better.
The fixture cutsheet (link above) says "removable lens for easy access to LED module and electrical components". I have a call into the lighting vendor to get their take on this. If anyone has similar experience or thoughts on the matter I'd love to hear it. Thanks!
The electrical inspector is prohibiting the installation because the fixtures are close enough to the structure above that "an electrician cannot get access to the junction box of the fixture without needing to bring the entire fixture down". The existing fluorescent fixtures (that were wired through knockouts on the fixture ends) were legal per the electrical inspector, because you could get access to the wiring by opening the door. I have not been to the site yet to view the new fixture.
We have the option to retrofit the fluorescent housing. The existing fixtures have not yet been removed, and the client has enough lighting replacement projects in the works that the LEDs would have a home by next summer. So this isn't that painful. But it's weird, as one of the original selling points for LED troffers was you can slip them into tighter ceilings. It's one more thing I would have to wonder about when looking at replacement of an existing recessed system, and the less things I have to wonder about the better.
The fixture cutsheet (link above) says "removable lens for easy access to LED module and electrical components". I have a call into the lighting vendor to get their take on this. If anyone has similar experience or thoughts on the matter I'd love to hear it. Thanks!