RWC/NC.
Senior Member
- Location
- N.Carolina
- Occupation
- Electrical
Gentlemen, this being after the fact & the Original Poster already having his answer.
But keep forgetting, not everyone's on the 2020 addition NFPA 70
*Seeing some are on 2017 and another on 2014. *So realizing my statement in post #5 being non-effective to previous addition(s). So going post entirely Article 410/ New Section #118.. This being something of expectations, if/when 2020 addition being adopted into your area.
(N) 410.118 Access to Other Boxes.
Luminaries recessed in ceilings, floors, or walls shall not be used to access outlet, pull, or junction boxes or conduit bodies, unless the box or conduit body is a integral part of the listed Luminarie..
But keep forgetting, not everyone's on the 2020 addition NFPA 70
*Seeing some are on 2017 and another on 2014. *So realizing my statement in post #5 being non-effective to previous addition(s). So going post entirely Article 410/ New Section #118.. This being something of expectations, if/when 2020 addition being adopted into your area.
(N) 410.118 Access to Other Boxes.
Luminaries recessed in ceilings, floors, or walls shall not be used to access outlet, pull, or junction boxes or conduit bodies, unless the box or conduit body is a integral part of the listed Luminarie..