I have a customer who wants LED strip under her entire deck railing. One section is 75' long and the other section is about 25' long.

If I fed the center of the 75' run should I be ok with this this length? I have never done such a long, continuous run.

thanks
Brett
 
The driver specs will tell you the length and wattage the driver will support.
The driver spec's will limit the wattage. 60W max for 12 volt or 96W max for 24V to be Class 2 but it will not give you a maximum tape length. You need to look at the tape specs for the maximum run. Tape wattage can very from roughly 1W to 6W per foot.
 
The driver spec's will limit the wattage. 60W max for 12 volt or 96W max for 24V to be Class 2 but it will not give you a maximum tape length. You need to look at the tape specs for the maximum run. Tape wattage can very from roughly 1W to 6W per foot.
I put in some UC lights a few years ago and the driver absolutely gave a max distance. The lights and driver were the same brand. I can't remember the brand as the HO ordered them.
 
My biggest concern for long runs, is not voltage drop, but conductor size. How much current will the little flat strip tying the LED’s together handle? You know the manufacturer is using the smallest possible.
 