can you experts tell me if this is legal or ever been legal.
older home probably built in 1940'-50' 3850 sf with small 600 sf detached apartment. 200 amp overhead service hits meterbase on side of house then go's into basement all in rigid conduit, wire size 2/0 copper. in the basement it go's into a 6"x6"x2' gutter where it is tap to feed one 200 amp panel & one 100 amp panel. i think the service entrance conductor should be sized for 300 amp. i did a load calc i came up with 207 amps. its a kitchen remodel job not adding much in load, a couple of can lights & refeeding appliances at there new locations. i'm recommending upgrading the service to a 320 amp.
thanks for any input
older home probably built in 1940'-50' 3850 sf with small 600 sf detached apartment. 200 amp overhead service hits meterbase on side of house then go's into basement all in rigid conduit, wire size 2/0 copper. in the basement it go's into a 6"x6"x2' gutter where it is tap to feed one 200 amp panel & one 100 amp panel. i think the service entrance conductor should be sized for 300 amp. i did a load calc i came up with 207 amps. its a kitchen remodel job not adding much in load, a couple of can lights & refeeding appliances at there new locations. i'm recommending upgrading the service to a 320 amp.