legal or not

Status
Not open for further replies.

rickl

Senior Member
can you experts tell me if this is legal or ever been legal.
older home probably built in 1940'-50' 3850 sf with small 600 sf detached apartment. 200 amp overhead service hits meterbase on side of house then go's into basement all in rigid conduit, wire size 2/0 copper. in the basement it go's into a 6"x6"x2' gutter where it is tap to feed one 200 amp panel & one 100 amp panel. i think the service entrance conductor should be sized for 300 amp. i did a load calc i came up with 207 amps. its a kitchen remodel job not adding much in load, a couple of can lights & refeeding appliances at there new locations. i'm recommending upgrading the service to a 320 amp.
thanks for any input
 
I would say it was legal at the time it was installed (though before I existed).
 
Last edited:
Having the 2/0 coper supply a 200 and 100 amp service panel is 'legal' today.

See 230.90(A) Exception No. 3.

However the the calculated load must not exceed the ampacity of the conductors.

Your 2/0 copper is most likely rated 175 amps.

Time for a 400 amp service with a class 320 meter.

Of course you could leave the existing panels, replace the meter socket with a class 320 and replace the conductors with 4/0 copper for a rating of 230 amps.
 
Bob, what you said about 2/0 being good for 175 amps makes me wonder about something..

table 310.15 B 6 tells us that we can use 2/0 copper for services on single family dwellings..

does that mean that i can use that 2/0 for the riser AND between the meter and first point of disconnect, or just the riser (mast) ?

and on hooking up mobile homes, generally we set a pole with a meter/main combo, and pull 4 wires underground to the mobile home. on a 200 amp service, can we pull 2/0 between that disconnect and the mobile home, or should it be 3/0 ?
 