legal use of plastic covered cable on bus duct disconnec
joe rodriguez
New member
My present employer wants to use plastic covered cable to disconnect overhead bus duct disconnect switchs instead of the insulated fiber pole. I refused to alter the safe way to disconnect the switchs and was told that the companys safety officer checked with OSHA and they allow this installation of cable for disconnect use. The company is located in Delaware ,can any one verify this change in safety and if not is there a code that I can inform them that this is illegal and unsafe. [*]
Re: legal use of plastic covered cable on bus duct disconnec
368.12 Feeder or Branch Circuits.
Where a busway is used as a feeder, devices or plug-in connections for tapping off feeder or branch circuits from the busway shall contain the overcurrent devices required for the protection of the feeder or branch circuits. The plug-in device shall consist of an externally operable circuit breaker or an externally operable fusible switch. Where such devices are mounted out of reach and contain disconnecting means, suitable means such as ropes, chains, or sticks shall be provided for operating the disconnecting means from the floor.
why would an insulated cable be less safe than a fiberglass pole?
why would it even need to be insulated?
[ November 19, 2005, 09:20 PM: Message edited by: petersonra ]