For lay in troffers, is there a max. length of whips to each light from a j box ? It seems like I remember reading 6' somewhere. Thank you.
But MC is ok, right ?6' is the limit when using 3/8" FMC. {348.20(A)(2)}
Yes MC cable is not a raceway and can be used in any length as branch circuit wiring.But MC is ok, right ?
Can you expand on this? What kind of cord are you referring to?If you are using portable cord, the distance is dependent upon the gauge of the cord being used.
Article 400.Can you expand on this? What kind of cord are you referring to?
Actually those are probably part of the listed assembly. I have seen these fixtures come with short cords which would not be governed by article 400. Back to the OP's scenario, cords covered by article 400 would not be allowed in any length above the ceiling for fixture whips.Article 400.
Coincidentally, I just walked by these today at a commercial building. I was surprised to see this use just inches from a sidewalk where little people or snow machines could come in contact. This would seem to be a violation imo of 400.8, but perhaps not.
Totally glossed over the "lay in troffers" piece...LOL. Yes, those are likely part of the listed assembly, there are many examples. But wouldn't Article 400 cover you in making your own similar portable cord stub to connect a similar assembly that didn't come with a connecting cord?Actually those are probably part of the listed assembly. I have seen these fixtures come with short cords which would not be governed by article 400. Back to the OP's scenario, cords covered by article 400 would not be allowed in any length above the ceiling for fixture whips.
No, and certainly not for troffers in a suspended ceilingTotally glossed over the "lay in troffers" piece...LOL. Yes, those are likely part of the listed assembly, there are many examples. But wouldn't Article 400 cover you in making your own similar portable cord stub to connect a similar assembly that didn't come with a connecting cord?
I understand NO for troffers, as 400 clearly states that. But are you also saying NO for installations similar to that in the picture?No, and certainly not for troffers in a suspended ceiling