Hello all,
I have a situation where I have a 5k rated contactor who fault is calculated at 9k using the point to point method. I have an availiable fault at the service of 40k and the panel where the contactor is being used is fed with 400A class "RK1" fuses which limit the current to 10k.
My question is can I use the 10k to do my point to point calculation or does this just mean that the fault anywhere down that line can not be greater than 10k?
It is a 480V 3 phase system.
I have a situation where I have a 5k rated contactor who fault is calculated at 9k using the point to point method. I have an availiable fault at the service of 40k and the panel where the contactor is being used is fed with 400A class "RK1" fuses which limit the current to 10k.
My question is can I use the 10k to do my point to point calculation or does this just mean that the fault anywhere down that line can not be greater than 10k?
It is a 480V 3 phase system.