I have a situation where a new service was installed, the available fault current at the load side of the service disconnect at a main lug panel is 50k, and 22k branch breakers were installed. i failed the installation, the engineer sent me a calculation that the let thru current of the current limiting fuses at the service disconnect is 14k at the main lug panel and says that panel is fully rated, i disagree, i say he must use a series rated combination or fully rated would be branch breakers rated 50k or more, I have cited 240.86 but he disagrees, looking for some info, thanks in advance