Re: Lets have some fun.
When I started typing this comment, I had planned to play along on southernboys-2's side for a while. But before I finished typing, I had talked myself into supporting those who had said that 210.8 did not apply to the fan's receptacle.
Presuming there is a receptacle attached to, and a component part of, the ceiling fan, then that receptacle is not, by the NEC's definition, a "receptacle." Look at the Article 100 definition of "receptacle," and take special note that it contains the word "at."
A receptacle is a contact device installed at the outlet for the connection of an attachment plug.
So is the fan's receptacle installed "
at the outlet"? You must look at the definition of "outlet."
A point on the wiring system at which current is taken to supply utilization equipment.
So you connect the fan's supply wires to the premises wiring system. At that point, you are not longer
at the outlet. Internal to the equipment, there are wires that connect to what looks to all the world like a receptacle. But that (apparent) receptacle is not installed
at the outlet, so it does not meet the NEC's definition of receptacle. Therefore, 210.8 would not require it to be GFCI protected.
QED