Re: Lets have some fun.
Nothing stops some people.
Nothing stops some people.
Jim you have to stop calling this device a 'receptacle' it is not a receptacle to the NEC any more than a 'trash receptacle' is a receptacle to the NEC.Originally posted by jimwalker:
So if this receptacle is not for taking current then why is it even there.
Then of course there is this.406.2 Receptacle Rating and Type.
(A) Receptacles. Receptacles shall be listed for the purpose and marked with the manufacturer?s name or identification and voltage and ampere ratings.
(B) Rating. Receptacles and cord connectors shall be rated not less than 15 amperes, 125 volts, or 15 amperes, 250 volts, and shall be of a type not suitable for use as lampholders.
If the fan was above a shower and that fan disconnecting means was a receptacle there is this problem406.3 (A) Grounding Type. Receptacles installed on 15- and 20-ampere branch circuits shall be of the grounding type. Grounding-type receptacles shall be installed only on circuits of the voltage class and current for which they are rated, except as provided in Table 210.21(B)(2) and (B)(3).
So if you insist this fan outlet is a receptacle you have many violations not just 210.8.406.8 (C) Bathtub and Shower Space. A receptacle shall not be installed within a bathtub or shower space.
Originally posted by roger:
Jim, if you are that determined to use this for your hair dryer go for it.![]()
Roger
Thats true, it is also evolution at work.Originally posted by jimwalker:
Nothing stops some people.
Haven't you been having fun all along?Originally posted by electricmanscott:
Wasn't the title of this thread "Let's have some fun"? Ok I'm ready. Let's get started.
We alredy are. Can't you picture Jim in the middle of the bathroom floor with his hairdryer plugged into the ceiling? :roll:Originally posted by electricmanscott:
Wasn't the title of this thread "Let's have some fun"? Ok I'm ready. Let's get started.
Originally posted by electricman2:
We alredy are. Can't you picture Jim in the middle of the bathroom floor with his hairdryer plugged into the ceiling?![]()
Who says Jim is a man? :roll:Originally posted by iwire:
I'm having a good laugh just thinking of a man with a hair dryer.![]()
Who says Jim has hair?Originally posted by LarryFine:
Who says Jim is a man? :roll:Originally posted by iwire:
I'm having a good laugh just thinking of a man with a hair dryer.![]()
I can touch the line side of the GFCI located beside the sink if I take the time to REMOVE THE COVER!Originally posted by jimwalker:
Why do these fans even have this type of connection that could be misused ?
Bob i don't believe you cold touch the line side.Have you actually done this ?Originally posted by iwire:
I can touch the line side of the GFCI located beside the sink if I take the time to REMOVE THE COVER!Originally posted by jimwalker:
Why do these fans even have this type of connection that could be misused ?![]()
Why are panel covers held in place with screws?
Why not weld the covers on to save people from themselves?![]()
And while we are wondering about these safety issues why don't they fence in the sides of all streets so I do not walk off the sidewalk into traffic?![]()
I think you may have missed the point of my post.Originally posted by jimwalker:
Bob i don't believe you cold touch the line side.Have you actually done this ?
Exactly, some folks can not be saved from themselves no mater what we do.Originally posted by jimwalker:
Nothing stops some people.
Jim, believe it or not, we're required by our quasi-OSHA inspectors to install cover on our temp GFI's on the rough, because "OSHA thinks someone with a screwdriver in their hand plugging in a cord could get shocked." I am not making this up.Originally posted by jimwalker:
Bob i don't believe you cold touch the line side. Have you actually done this?Originally posted by iwire:
I can touch the line side of the GFCI located beside the sink if I take the time to REMOVE THE COVER!![]()
Do you feel a plate is required for the finish inspection?Originally posted by georgestolz:
believe it or not, we're required by our quasi-OSHA inspectors to install cover on our temp GFI's on the rough, because "OSHA thinks someone with a screwdriver in their hand plugging in a cord could get shocked."
I agree with your thought but we can not look at it that way.Originally posted by georgestolz:
I just think the premise is ridiculous. GFI's occupy so much of the surface area of the box, it would be a feat to make contact with the screws.
Not really. Every panel I install has a dotted cut-out on the back of the box and is referred to as a "plaster shield" to protect the internals during construction. Someone could easily plead ignorance based on encouragement from the manufacturer.Originally posted by iwire:
By the way, putting cardboard over the panel instead of the panel cover is likely to a change a simple violation to a 'willful violation'.
George, that's pretty weak. I realize we live in a blame society, but a prefessional electrician could never plead to be so ignorant as to use a cardboard cutout as a deadfront. :roll:Originally posted by georgestolz:
Every panel I install has a dotted cut-out on the back of the box and is referred to as a "plaster shield" to protect the internals during construction. Someone could easily plead ignorance based on encouragement from the manufacturer.