Leviton Arc-Fault tripping on LED lighting.

makesends

New User
Location
Oregon
Occupation
Electrical/Electronics Tech
In my last job, almost all the lighting the customer wanted is LED, so I ran most of the house lighting on two 15amp lighting circuits. They also wanted the Leviton breaker panel (which, otherwise, I do too). The problem is that though neither breaker is overloaded (RMS current), at some point both breakers trip according to the number of fixtures/ amount of load on Arc-Fault only. It usually happens on starting, for example, undercabinet lights. The inspector says I must have arc fault protection even on the lighting circuit over living areas, even though they have no receptacles involved.

My question is, would a choke/reactor on the line solve the problem, or is there some other suggestion you might have? I'm guessing the breaker is reading the accumulation of switching mode power supplies in the fixtures as arcing. These people also have two bedrooms they will be using as offices (therefore, Arc Fault breakers on the related receptacles. I'm dreading what those computers and servers will do.
 
Do the lighting circuits have dimmers? Sometimes they can contribute to AFCI tripping issues.

I came across a video where a blank face AFCI was used instead of an AFCI breaker because it was apparently less susceptible to tripping on certain loads:

 
Parallel arc and series arc are very easy to distinguish on the diagram, but everything is series in reality. The distinction can get blurry.

Series is something sensed like a bulb that's turned on, but flickering because of a loose connection.
Parallel is something sense as a bulb that's off, but flashing briefly as it makes intermittent unintended connection and causing it to come on.

There is a legitimate arc every time you interrupt a flow of current with a mechanical switch but this should be ignored, but if it happens repeatedly in a small amount of time or it goes on for a long time, the AFCI will trip. The decision making process is depends how each AFCI is designed or configured.

The reason the guy in the YouTube video a few posts up mentions microwaves and clothes washers is that they have a current signature that some AFCIs interpret as one of the arc pattern. His idea is to get around it by using "some other" AFCIs hoping that they don't interpret the signals quite the same way.
 
Last edited:
The reason the guy in the YouTube video a few posts up mentions microwaves and clothes washers is that they have a current signature that some AFCIs interpret as one of the arc pattern. His idea is to get around it by using "some other" AFCIs hoping that they don't interpret the signals quite the same way.
And we shouldn't have to put up with this.

I'm not against what they are trying to accomplish with AFCI, but they have made the consumer part of their long term testing lab and many installers have had to eat costs on it and they still haven't perfected this technology yet. they maybe have replaced some devices for no charge, they probably have not reimbursed much or even any man hours for this nonsense though.
 
In my last job, almost all the lighting the customer wanted is LED, so I ran most of the house lighting on two 15amp lighting circuits. They also wanted the Leviton breaker panel (which, otherwise, I do too). The problem is that though neither breaker is overloaded (RMS current), at some point both breakers trip according to the number of fixtures/ amount of load on Arc-Fault only. It usually happens on starting, for example, undercabinet lights. The inspector says I must have arc fault protection even on the lighting circuit over living areas, even though they have no receptacles involved.

My question is, would a choke/reactor on the line solve the problem, or is there some other suggestion you might have? I'm guessing the breaker is reading the accumulation of switching mode power supplies in the fixtures as arcing. These people also have two bedrooms they will be using as offices (therefore, Arc Fault breakers on the related receptacles. I'm dreading what those computers and servers will do.
A few years ago I was working with a guy who had rented the Dranetz German power quality meter (really expensive high end) and he was bewildered by the readings of an LED light bulb. It had a massive power spike and horrible power factor loss for a nano second when turning on. The current load switching on was 9X of the actual energy when on. I didn't believe it, what I was seeing. We ran this test on other LED bulbs, fixtures and found all kinds of different readings, but the same deal: Massive power factor loss and nano second current spike.
 
A few years ago I was working with a guy who had rented the Dranetz German power quality meter (really expensive high end) and he was bewildered by the readings of an LED light bulb. It had a massive power spike and horrible power factor loss for a nano second when turning on. The current load switching on was 9X of the actual energy when on. I didn't believe it, what I was seeing. We ran this test on other LED bulbs, fixtures and found all kinds of different readings, but the same deal: Massive power factor loss and nano second current spike.
Tungsten filament lamps have just as high or even higher inrush on a cold start. They are linear current devices though and likely not going to cause as much issues with GFCI/AFCI's
 
A few years ago I was working with a guy who had rented the Dranetz German power quality meter (really expensive high end) and he was bewildered by the readings of an LED light bulb. It had a massive power spike and horrible power factor loss for a nano second when turning on. The current load switching on was 9X of the actual energy when on. I didn't believe it, what I was seeing. We ran this test on other LED bulbs, fixtures and found all kinds of different readings, but the same deal: Massive power factor loss and nano second current spike.
Tungsten filament lamps have just as high or even higher inrush on a cold start. They are linear current devices though and likely not going to cause as much issues with GFCI/AFCI's

Here's the thing though, while software driven devices allow for post-production defect removal (affectionately called "firmware update"), they're insanely unreliable for critical applications.

Solid state landline phones with push buttons may contain some digital circuitry, but those devices are not embedded systems crap driven, they may experience issues that you can't ever resolve, but they're not prone to the reliability issues of modern software driven smartphones that suffer from occasional latch-ups that require rebooting.

Modern software based design allows for firmware updates and adaptive learning, but they suffer significantly higher chance of glitches, like software hang-ups that makes the device fail to trigger. False negative is simply unacceptable for AFCIs, but without software driven system that puts it at risk of such, AFCIs suffer from hard-coded vulnerabilities to some false positives that can only be resolved by redesigning the circuitry.
 
I had a microwave on a dedicated circuit that kept nunance tripping AFCI. I Changed it out with the microwave in the other break room. Just swapped. Everything new and all equipment the same, Problem went away. I was never sure what caused it, identical microwaves, identical panels, identical AFCI
 
I had a microwave on a dedicated circuit that kept nunance tripping AFCI. I Changed it out with the microwave in the other break room. Just swapped. Everything new and all equipment the same, Problem went away. I was never sure what caused it, identical microwaves, identical panels, identical AFCI
Now the question arises. Which one was working properly?
 
Now the question arises. Which one was working properly?
Yeah good question. I couldn't find anything wrong. I know it happened right as soon as the start button was touched. The only thing I'm not sure of is if they were both on the same phase of the 208/120 wye.
 
A few years ago I was working with a guy who had rented the Dranetz German power quality meter (really expensive high end) and he was bewildered by the readings of an LED light bulb. It had a massive power spike and horrible power factor loss for a nano second when turning on. The current load switching on was 9X of the actual energy when on. I didn't believe it, what I was seeing. We ran this test on other LED bulbs, fixtures and found all kinds of different readings, but the same deal: Massive power factor loss and nano second current spike.
A few years back I was working on a project in our shop which used (4) 24VDC LED lights powered by a 24V traction battery in a "Tugger" (factory vehicle for pulling carts). They were relatively small lights, and drew a combined ~4A when ON. Long story short, I come to find out the inrush for those lights was ~140A !! It caused problems with the relay that turned them on and off (it would typically weld the contacts closed).

Like Herding_Cats describes in post #12, I found the whole inrush event was incredibly short. The spike was gone by ~0.25 msec. I assumed it was poor design that had no - or nearly none - current limiting when first charging up whatever caps were in the internal LED power supply. They simply appeared like a Black Hole when the 24V first came up.

It was an interesting problem to have to solve, made worse by the fact they are DC powered. I can try to write up a separate thread about it - if anybody would find it interesting. I still have the data and scope traces I'm sure.
 
Now the question arises. Which one was working properly?
You could buy two units of identical washers, yet they could sound different enough that you could tell which unit is running. What AFCIs look for is similar to "acoustic signature". If you were to pass one of the lines through a current transformer and feed the CT into a speaker, you would have an acoustic signature. That's what the AFCI is listening into.
 
A few years back I was working on a project in our shop which used (4) 24VDC LED lights powered by a 24V traction battery in a "Tugger" (factory vehicle for pulling carts). They were relatively small lights, and drew a combined ~4A when ON. Long story short, I come to find out the inrush for those lights was ~140A !! It caused problems with the relay that turned them on and off (it would typically weld the contacts closed).

Like Herding_Cats describes in post #12, I found the whole inrush event was incredibly short. The spike was gone by ~0.25 msec. I assumed it was poor design that had no - or nearly none - current limiting when first charging up whatever caps were in the internal LED power supply. They simply appeared like a Black Hole when the 24V first came up.

It was an interesting problem to have to solve, made worse by the fact they are DC powered. I can try to write up a separate thread about it - if anybody would find it interesting. I still have the data and scope traces I'm sure.
Yeah, that's common. See: https://www.digikey.com/en/articles/compact-fluorescent-tribulations

Years back, industrial power supplies used for automations and such with tens of thousands of uF of rectifier (pre PFC days) had enough inrush to magnetic trip a branch breaker. Some were actually designed with a large power resistor in series. It was powered up through a resistor, then a TRIAC or relay would short across the resistor after a few seconds and the whole thing was wired through a thermal fuse that was attached to the power resistor so that the whole thing doesn't catch on fire in case the relay/TRIAC failed to close.

These days, a lot of LED lamps have a permanent 10 ohm resistor in series with the ballast on the line input which is low enough to be insignificant with how much power they use these days, but high enough to avoid undesirable levels of inrush. Take a look sometime.

You'll also find that these days, things that use an electronic switch (push button or touch screen) utilizes soft start. Things like cordless vacuums. MOSFETs do not like the inrush associated with directly attaching the motor to power source. Also, in order to conserve battery life, battery powered vacuums and such are designed to be turned off/on often rather than idle and repeated across-the-line starting is bad for brush life and battery consumption.
 