Leyton transformer connections

Status
Not open for further replies.

Smart $

Esteemed Member
Location
Ohio
Try harder....
Doing so just reaffirms the power is not balanced. I see power distributed among windings... but nowhere close to being balanced. A single-phase load sees the direct winding as 1z and the indirect windings as 2z. Where's the balance?
 

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
A transformer has Pin = Pout instantaneously as long as you are not considering the magnetizing current, which will be pumping energy into the core and pulling it out again, just like an ideal inductor or capacitor.
OK, so the Leyton configuration uses the magnetic field of the core like an inductor to store energy during part of the cycle, thereby transforming the constant power delivery of the balanced 3 phase Pin into the double frequency sinusoidal (offset, with non-zero average) single phase power Pout?

Cheers, Wayne
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
Doing so just reaffirms the power is not balanced. I see power distributed among windings... but nowhere close to being balanced. A single-phase load sees the direct winding as 1z and the indirect windings as 2z. Where's the balance?

The description notes that if you use identical transformers (which you do not have to do) some paths will have twice the coil resistance. But this affects only the magnitude of the power losses, which are in the 1-5% range, not the load current and power.
To my mind a current distribution of 100:98:98 is close enough to balanced to keep everybody happy.
If not, just double the wire size for the indirect windings. Then totally balanced.

mobile
 

Smart $

Esteemed Member
Location
Ohio
The description notes that if you use identical transformers (which you do not have to do) some paths will have twice the coil resistance. But this affects only the magnitude of the power losses, which are in the 1-5% range, not the load current and power.
To my mind a current distribution of 100:98:98 is close enough to balanced to keep everybody happy.
If not, just double the wire size for the indirect windings. Then totally balanced.
:blink: The 2 circuit wires for the indirect windings' current are the same 2 circuit wires that carry the direct winding's current.


When the current carried by those 2 wires reaches node "a" on one side of the transformer secondary it sees the indirect windings as a 2z impedance and the direct winding as a 1z impedance, divides accordingly then through the parallel pathways provided by the windings only to recombine at node "c", then back out to and through the load where the loop is thus completed.
 