LFMC as service raceway

Status
Not open for further replies.

yetiman

Member
In article 230.43(15) it says you can use LFMC as a service raceway if under 6' and an equipment bonding jumper is used routed with the conduit. My question then is if you are useing this method between the meter and the service disconnect (200a),what exactly would this look like. Do you use bonding bushings at each end of the LFMC, then bond to each enclosure to make sure the fittings are properly bonded or can you just bond as a regular equip. ground to each can? Or bond the 2 fittings with a jumper then to either the meter enclosure or disconnect. It refers back to 250.102 which normaly you would use a jumper from a bonding bushing. I haven't had someone want to use LFMC as a service raceway before. Opinions?
 
There's special LFMC connectors that have a bond lug on them.

EDIT: see the left most connector, and reference attached catalog pages"

TopbarProducts3.gif


http://www.o-zgedney.com/PDF/GB[1].pdf
 
Last edited:
So, you bond both ends of the LFMC with a jumper routed with the service conductors and then to either enclosure?
 
yetiman said:
So, you bond both ends of the LFMC with a jumper routed with the service conductors and then to either enclosure?
I don't know because I don't build services with LFMC. You can run the bonding jumper internal, if you want to, though. I was just pointing out that they make a special fitting to make it a little easier.
 
It certainly wouldn't do any harm to bond to both enclosures, so go ahead and do it. The extra $3 in material and 15 min may prevent you from either failing an inspection or spending 15 minutes discussing it with the AHJ.

The same goes for 2 ground rods...when in doubt, install 2.
 
yetiman said:
So, you bond both ends of the LFMC with a jumper routed with the service conductors and then to either enclosure?
You would bond the fittings and then to the enclosure and each end with the jumper run with the raceway.You would apply article 250.92 along with 250.43.
Rick
 
Bonding of the raceway could be accomplished by bonding one end of raceway. Neutral or (grounded conductor) is also the equipment bonding jumper for both meter and service disconnect. No seperate equipment bondiong jumper for the two enclosures is required unless your neutral (grounded conductor) is not bonded down in the meter and it will be bond at the service enclosure by the main bonding jumper required in 250.28.
But as Tom said sum locations my not permit this wiring method inside the lines of a structure.
 
Bea said:
Bonding of the raceway could be accomplished by bonding one end of raceway.
Bea, in the #6 post i quoted 250.43, but 230.43 requires to run the bonding jumper through the sealtight and bond both ends of the raceway.

(15) Flexible metal conduit not over 1.8 m (6 ft) long or liquidtight flexible metal conduit not over 1.8 m (6 ft) long between raceways, or between raceway and service equipment, with equipment bonding jumper routed with the flexible metal conduit or the liquidtight flexible metal conduit according to the provisions of 250.102(A), (B), (C), and (E) .
Rick
 