In article 230.43(15) it says you can use LFMC as a service raceway if under 6' and an equipment bonding jumper is used routed with the conduit. My question then is if you are useing this method between the meter and the service disconnect (200a),what exactly would this look like. Do you use bonding bushings at each end of the LFMC, then bond to each enclosure to make sure the fittings are properly bonded or can you just bond as a regular equip. ground to each can? Or bond the 2 fittings with a jumper then to either the meter enclosure or disconnect. It refers back to 250.102 which normaly you would use a jumper from a bonding bushing. I haven't had someone want to use LFMC as a service raceway before. Opinions?