I need to use LFMC in CLASS 1 DIV. 2 location between motor and explosion proof box, but I want to know if the following is enough
1- the total length of LFMC is less than 6ft.
2-OCPD is less than or equal to 10A.
3-The LFMC is listed for unclassified location with listed straight connector.
4-motor box and ex proof box are threaded with internal EGC.
5-There is ex proof union for grounding .
so, is there any need to use additional external bonding jumper or lockout for grounded and bonding issue ??
View attachment 8974View attachment 8977
also i hope to find clear and direct reply.
Thanx