LFMC support

Status
Not open for further replies.
Ok what do y'all think of this one. This is a PV system I did. Sorry for the not so great picture. This was a third party "quality" inspection from the state because the system was done under their incentive program. Code section cited was just 350.30, with the description "Circuit conduit or raceway lacks adequate support. Conduit is secured with plastic wire ties.". You can't tell from the picture, but these are the heavy duty 3/8 wide wire ties not the little skinny ones. I think it is hogwash.

What alternative could be used? I thought about a minerallac, but I think that would look awful. Maybe a hose clamp?

I'm actually not going to "fix" it, as it is a minor enough violation they are not requireing photo documentation that it was changed.
 

Attachments

  • IMG_5111.JPG
    IMG_5111.JPG
    123.2 KB · Views: 44

Ponchik

Senior Member
Location
CA
Occupation
Electronologist
Bolt a 6" wide board on the back of the "U"channel and use two hole strap to support the conduit to the board.

Some inspectors "HAVE" to say something, because they can't find anything to cite.
 

Chamuit

Grumpy Old Man
Location
Texas
Occupation
Electrician
He's got you. If the inspector is an agent of the AHJ and he doesn't approve, you need to comply.

1678889695889.png
 
He's got you. If the inspector is an agent of the AHJ and he doesn't approve, you need to comply.

View attachment 2564430
Well this is an interesting situation. It's not real clear-cut who is the AHJ here. Here in upstate New York we have private third party electrical inspectors, so I would say they are the AHJ. My electrical inspector passed/approved this. The state agency that distributes the rebates has some sort of stake in it but I would have to go through the program manual to look at the exact wording.
 

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
350.30(A) (2017 and later) specifically allows cable ties "listed and . . . identified for securement and support" on LFMC. So did you use the correct type? If so I suggest supplying the code reference and documentation on the cable ties used.

Cheers, Wayne
 
350.30(A) (2017 and later) specifically allows cable ties "listed and . . . identified for securement and support" on LFMC. So did you use the correct type? If so I suggest supplying the code reference and documentation on the cable ties used.

Cheers, Wayne
Oh interesting I forgot about that, I was looking at the 2014 just because I had that handy. Which or how many cable ties are listed for support?
 

Electromatic

Senior Member
Location
Virginia
Occupation
Master Electrician
I've wondered the same thing about cable ties. Many wiring methods mention them in their .30 sections, always saying "listed and identified". Do they need some kind of electrical listing for each cable or conduit type? If the package identifies them as capable of supporting _x_lbs., does that suffice?
 
I've wondered the same thing about cable ties. Many wiring methods mention them in their .30 sections, always saying "listed and identified". Do they need some kind of electrical listing for each cable or conduit type? If the package identifies them as capable of supporting _x_lbs., does that suffice?
Capable of supporting _x_lbs works for us.

Is there a listing standard for cable ties used as conduit support? How many pounds strength would I need? Is that defined somewhere? This seems like another genius CMP move to me.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Is there a listing standard for cable ties used as conduit support? How many pounds strength would I need? Is that defined somewhere? This seems like another genius CMP move to me.
Yes there is. The following is from the UL Guide Information for Positioning Devices (ZODZ).
Type Classification
Type 2 or 21 – Products are investigated to maintain the declared loop tensile strength (cable ties) or mechanical strength (fixing devices) after environmental exposures.
Type 2S or 21S – Products are investigated to maintain the declared loop tensile strength (cable ties) or mechanical strength (fixing devices) after environmental exposures. Strength is retained for a prolonged specified time and are suitable for use as primary support of flexible conduit, flexible tubing, or cable as defined in ANSI/NFPA 70, "National Electrical Code" (NEC). Declared strength shall be at least 220 Newtons (50 lbs). Such product may be marked “Support” in lieu of the “S” designation.
 

jap

Senior Member
Occupation
Electrician
Looks good to me, although I'd of probably hard piped the whole thing.

JAP>
 

synchro

Senior Member
Location
Chicago, IL
Occupation
EE
It's pretty common to use LFMC to PV inverters. Sort of like how we use flex to transformers - not really sure it's necessary or why we do it but why change 🙃

Is the conduction of noise through hard piped conduits ever an issue? If so, it's probably less of a problem with the usual "transformerless" inverters.
 
Status
Not open for further replies.