What is the max length for LFMC in CLASS 1 DIV.2 locations, if there is an internal internal EGC between the motor and the control panel??
 

stev11

Member
Location
india
What is the max length for LFMC in CLASS 1 DIV.2 locations, if there is an additional internal EGC (ground wire)between the motor and the control panel??
 

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
Except for the prohibition against double-locknut and locknut-bushing means of bonding, there are no other restrictions for LFMC beyond those of Article 350 in Division 2. For your particular interest see Section 350.60; read and understand the cross-references as well.
 

stev11

Member
Location
india
Except for the prohibition against double-locknut and locknut-bushing means of bonding, there are no other restrictions for LFMC beyond those of Article 350 in Division 2. For your particular interest see Section 350.60; read and understand the cross-references as well.

thank you.
but I read your reply in the below link, and your reply #18
http://forums.mikeholt.com/showthread.php?t=154279&page=2


?
but, how can use(install) LFMC in unlimited length without a problem with ground-fault current path ???




LFMC cannot be used in an unlimited length either with or without a bonding jumper in a hazardous location. In unclassified locations study Article 350.



s
o, do you mean that it is permitted to use LFMC with unlimited length in C1D2!!

plz I need your help with clear reply.
 

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
I'm not going to do your homework for you. I'm not going to do your design without a significant consulting fee.

This is a simple as I can make it if you aren't willing to do the homework:
  • You cannot use a double-locknut or locknut-bushing alone to bond anything including LFMC and Section 501.30(B) Exception.
  • No matter how you bond it, the LFMC will be in the ground-fault path to some degree.
  • IF you intend to use LFMC as the "sole" EGC in a Division 2 location, it still must be installed per Article 350 and Section 250.102 with their appropriate cross-references AND:
    • it must be less than 6' with an external bonding jumper OR
    • it must have an internal bonding jumper and length is unspecified; however Article 350 and Section 250.102 with their appropriate cross-references still apply.
 