Lighitng control by fire alarm system

Status
Not open for further replies.

anbm

Senior Member
Location
TX
Occupation
Designer
In a hospital, we read from one of the owner stanadards is public lighting shall be controlled via fire alarm system, does anyone know how this work?
 
Let me rewrite the rule they enforce again:

"Exterior lighting" to be controlled via fire alarm system instead of time clock.

I am not sure how this comply with IECC rule.
 
Let me rewrite the rule they enforce again:

"Exterior lighting" to be controlled via fire alarm system instead of time clock.

I am not sure how this comply with IECC rule.
Unless I'm missing something, why can't you use both? Shunt the time clock with a FA relay.
 